The F6C800-UNV UPS was not designed to be serviced by the user, but the batteries it contains will inevitably fail after a few years and cripple the unit. With reasonable care however, the batteries can be replaced and the UPS given a new lease on life.
The UPS contains two Sealed Lead Acid (SLA) batteries rated at 12V, 7Ah with 0.25 inch wide Faston terminals. The original batteries in my unit were manufactured by Ritar, part number (PN) RT1270, although equivalent components are readily available from other manufacturers such as:
PowerSonic, PN PS-1270-F2 (See dimensions at the end of this procedure).
Yuasa, PN NP7-12
Rhino, PN SLA7-12
Werker, PN WKA12-7.5F2
I was able to find a vendor in my area (Northern Virginia) that had batteries in stock for a price of just over $12.00 each.
To replace the batteries, refer to the figure below and perform the following steps:
1. SAFETY FIRST! Make sure the unit is powered off and unplugged from the AC source.
2. Detach the cover by removing five screws (four on the bottom, one on the back).
3. Remove the cover by sliding it backward, taking care not to touch any main Printed Circuit Board (PCB) contacts with it.
4. Disconnect the following leads: RED lead to the transformer, BLACK lead to the main PCB, and BLACK lead interconnecting the two batteries.
5. Disconnect the front panel connector from the main PCB.
6. Remove the four screws that attach the main PCB (two front, two rear).
7. Remove the two screws that attach the battery bracket to the front plate using an offset (right-angle) screwdriver. It may be necessary to reposition the self-stick ty-rap mount that affixes the large EMI suppression ferrite.
8. Remove the two 9/32 inch nuts that attach the battery bracket to the bottom plate.
9. Move the battery bracket up just enough to allow the rear battery to be slid out the side of the unit. Temporarily reposition the main PCB if necessary. Do not allow the battery terminals to short against any metal parts.
10. Slide the front battery to the rear of the bracket and remove as above. Do not allow the battery terminals to short against any metal parts.
11. Insert the new batteries and reverse the steps listed above to complete the installation. Carefully align the bracket mounting screws (in step 7 above) to avoid cross-threading.
12. Connect the UPS to an AC source and turn the unit on. Run a 10-second self test after the batteries have charged for several hours.
13. For future reference, I recommend that you place a label on the unit indicating the battery part number, rating, and date of change.
The UPS contains two Sealed Lead Acid (SLA) batteries rated at 12V, 7Ah with 0.25 inch wide Faston terminals. The original batteries in my unit were manufactured by Ritar, part number (PN) RT1270, although equivalent components are readily available from other manufacturers such as:
PowerSonic, PN PS-1270-F2 (See dimensions at the end of this procedure).
Yuasa, PN NP7-12
Rhino, PN SLA7-12
Werker, PN WKA12-7.5F2
I was able to find a vendor in my area (Northern Virginia) that had batteries in stock for a price of just over $12.00 each.
To replace the batteries, refer to the figure below and perform the following steps:
1. SAFETY FIRST! Make sure the unit is powered off and unplugged from the AC source.
2. Detach the cover by removing five screws (four on the bottom, one on the back).
3. Remove the cover by sliding it backward, taking care not to touch any main Printed Circuit Board (PCB) contacts with it.
4. Disconnect the following leads: RED lead to the transformer, BLACK lead to the main PCB, and BLACK lead interconnecting the two batteries.
5. Disconnect the front panel connector from the main PCB.
6. Remove the four screws that attach the main PCB (two front, two rear).
7. Remove the two screws that attach the battery bracket to the front plate using an offset (right-angle) screwdriver. It may be necessary to reposition the self-stick ty-rap mount that affixes the large EMI suppression ferrite.
8. Remove the two 9/32 inch nuts that attach the battery bracket to the bottom plate.
9. Move the battery bracket up just enough to allow the rear battery to be slid out the side of the unit. Temporarily reposition the main PCB if necessary. Do not allow the battery terminals to short against any metal parts.
10. Slide the front battery to the rear of the bracket and remove as above. Do not allow the battery terminals to short against any metal parts.
11. Insert the new batteries and reverse the steps listed above to complete the installation. Carefully align the bracket mounting screws (in step 7 above) to avoid cross-threading.
12. Connect the UPS to an AC source and turn the unit on. Run a 10-second self test after the batteries have charged for several hours.
13. For future reference, I recommend that you place a label on the unit indicating the battery part number, rating, and date of change.