A UPS is only really needed in areas with unreliable or very dirty power, some more rural regions dont have good power so they can help, but if you are in a region with reasonably good power then its not really needed, a good power strip with surge supression is generally sufficient. One important thing to note, all items connected to the system should pass through the same surge protector before touching the wiring in the wall, that means computer, monitor, speakers, printer, and ideally the router too.

danraies

Distinguished
Aug 5, 2011
940
0
19,160
Surge protectors are good, but UPSs are better. I wouldn't call them a necessity, but they're certainly good for peace of mind. Surge protectors do a decent job against surges and spikes, but UPSs are still better. A UPS has the advantage of letting you shut down your computer during a power outage, which is nice. However the real benefit of a UPS, in my opinion, is protection against brown out. Surge protectors are useless against low voltage situations and those can seriously damage your PC.
 
A UPS is only really needed in areas with unreliable or very dirty power, some more rural regions dont have good power so they can help, but if you are in a region with reasonably good power then its not really needed, a good power strip with surge supression is generally sufficient. One important thing to note, all items connected to the system should pass through the same surge protector before touching the wiring in the wall, that means computer, monitor, speakers, printer, and ideally the router too.
 
Solution

COLGeek

Cybernaut
Moderator
Is an UPS "required" or absolutely needed? No.

Does a UPS offer better protection than a surge suppressor in the event of a power failure? YES!!!!!!!!!!!!

The OP has a nice rig. If it were me, I would have on an UPS....period. I have all my systems on UPS connections and I have never had a power related failure since using them. Small price to pay for peace of mind.
 

westom

Distinguished
BANNED
Mar 30, 2009
931
0
19,160


Many others made recommendations by even ignoring manufacturer spec numbers. For example, spec numbers for a UPS are typically smaller than those for strip protectors. A UPS typically has near zero protection numbers. And just enough above zero that the most easily manipulated will recommend it as 100% protection.

Eventually a consumer learns that recommendations using subjective reasoning are best called a scam. No replacement exists for manufacturer numeric specs. Those spec numbers say that UPS does near zero surge protection. Your joules numbers probably describe grossly undersized protection.

You are asking about protection from hundreds of thousands of joules. Smaller surges are only noise. Are made irrelevant by protection already inside every appliance. To promote a scam, advertising and hearsay will forget to mention that existing protection. And ignore all numbers.

A UPS leaves appliances connected directly to AC mains when not in battery backup mode. Myths say a UPS will disconnect to protect from a surge. More numbers. Surges are done in microseconds. A UPS takes milliseconds to disconnect. Will that millimeter gap in a UPS stop what three miles of sky cannot stop? Numbers not found in a *subjective* UPS recommendation.

View those Belkin specs. 3780 joules means only 1260 joules and never more than 2520 absorb surges that are hundreds of thousands of joules. Damning numbers.

No way around over 100 years of well proven science. Protection is always about where energy dissipates. Any recommendation that does not discuss hundreds of thousands of joules is, at best, very suspect. A protector is only as effective as its earth ground – where hundreds of thousands of joules dissipate harmlessly. Any recommendation that ignores earth ground would be promoting a scam. An honest answer has been well understood and observed for over 100 years. Is found in products from more responsible companies. Costs tens or 100 times less money.

Best protection does not have obscene profit margins. Instead, it does what always exists in every facility that can never suffer damage. Is sold by more responsible companies including Intermatic, General Electric, Square D, Siemens, Keison, Leviton, or ABB. An effective Cutler-Hammer solution is sold in Lowes and Home Depot for less than $50. That means direct lightning strikes are absorbed harmlessly outside the building. That means all appliances are protected including bathroom GFCIs, dishwasher, and the air conditioner.

If you need protection, then everything must be protected. What most need protection during a surge? Smoke detectors. Only the 'whole house' solution (and 100 years of well proven science) protects that.
 
Someone is angry at UPSs...


Many of them have a surge suppressor built inline with the primary AC in to surge suppress everything connected to it, and a surge suppressors job is NOT to dissipate the energy, that is a suicide mission for anything, its job is to redirect the surge to ground and avoid dissipating any energy if at all possible.

Im going to refer you back to the jonnyguru thread from 2 years ago where you went on a similar rant against surge suppressors.
http://www.jonnyguru.com/forums/showthread.php?t=7011
 
Surge protector, or UPS is not going to protect from a Direct hit, BUT most come with a Policy you can cliam against.
O and don't forget any other outside lines that connect to your Compute. My Aunt lost her computer, not from the AC but from the phone line going into computer.

As to an UPS, I live in a fairly area, but I still get WAY to many power outages in the course of a year, many only a couple of sec duration. Normally these do not damage the computer, That is MB/PSU - what it will often take out is them Dag burn mechanical HDDs that just happent to be writting to (Good old murphy's law) the fat allocation table. So Yess I recommend them.

Just have my two computers on them, lost power, got beeps so had to shut the computer that was on down - would have been nice had I had the monitor on it. But Win 7 easy, right Hit Windows key, hit right arrow key, then hit enter. Computer didn't shut down, but luckly dawned on me, hit "Y" then Enter - Yup it was asking if I wanted to terminate some program.
 

COLGeek

Cybernaut
Moderator
Here is what I know. 2 weeks ago, we had severe weather in my area. What systems I had up and running when the power failure occured all executed a nice orderly shutdown. As a result, I had no data failures, corrupted hard drives, etc.

All was good to go when the power came back on. The cost of the UPS is way less than the cost to replace the guts of my rigs. Just something to think about...
 
First, She live in a rural area in Florida Trailer park, and was a good 10-> 15 years ago - Does not matter what should/was not inplace - Period.

2nd, I'm somewhat knowelable about Fat/fat32 ect. Might whant to prefix that with "SHOULD", not Will as I've lost som ntft drives do to interupped writes.

Don't forget the EM pulse can take a system out by inducing a voltage on the line
 
On the subject of a UPS in this application, be aware that Active PFC PSUs tend to be picky about their input waveforms. The step wave used by cheap UPS units often looks like bad power to such a PSU and it will shut off, even if the lamp on your desk remains at full brightness. True sine-wave UPS units tend to be expensive, but that is probably what you need here. I have read that the "truncated triangle" waveform used by the newer Cyperpower APFC UPS units will also work, although I have yet to personally try one.
 

secolliyn

Distinguished
May 3, 2006
297
0
18,810
We have UPS's on all of out hardware here at home and i remember i was playing my Xbox 360 listening to music on my PC and talking to some friends and all of a sudden myu light goes out and as it turns out we had a power outage in the area well my UPS powered my 32 in LCD TV, Xbox 360, 22in LCDand my Core i7 920 build with a 600Watt PS and did it for about 20 Min then i turned off the 360 and my TV and used my computer for another 40 min till the power came back on


To answer your question No but i would recommend one for sure
 
The UPS doesn't have to match the PSU size, per se, but it does need to match the load you expect it to carry. If your 1200W PSU will actually be pulling close to 1200W from the wall, then yes you'll need a UPS at least that big (don't forget 75W-100W for your monitor). If your PSU will only need 300W from the wall (hah, not with GTX580 SLI!), then you could size the UPS accordingly. You're going to need a big one for your rig.
 

Traildriver

Distinguished
Sep 10, 2010
587
0
19,160
I use APC XS1300. APC = American Power Conversion. Their site has a good sizing calculator.

Saved me thru several brownouts and a couple outages (and I live in a city). Peace of mind that makes it worth it. When a bad storm comes my way I shut it all down anyways, the UPS is for the day to day line fluctuations.
 
That would normally be refered to as a square wave, and the 270V jump seems excessive, as does 200V considering 120V AC power is a sine wave between 170 V and -170 V so effective voltage from that square wave would greatly exceed 120V.

You seem to have awful specific numbers you are pulling from, do you have any site or documents you suggest for those of us who wish to learn a bit more about UPSs these days? Im an electrical engineering major so i can make it through the marketing BS and find the useful stuff normally. Where did you learn most of your stuff about UPSs and surge suppressors?
 
I've seen some scope shots of UPS outputs; that's why I generally don't buy TrippLite any more. I've seen a waveform allegedly from one of the Cyberpower APFC units. Like they say, it is a truncated triangle, but it crosses the "0" line much like a sine wave does, rather than lingering there like some square waves. I doubt that waveform was a lie, BUT, nothing was said of the load conditions, which is why I didn't trust it until someone with an Active PFC PSU said it worked. That still doesn't tell me what the waveform really becomes under load, but at least the way it crosses zero isn't going to flake out an Active PFC PSU.
And, in the middle of a game, a system with an OC'ed 2500K and a pair of GTX580 GPUs could well be pulling 700W or more.

Edit: Toss in the monitor, speakers, and maybe a CFL desk light, and you're probably over 800W. Multiple monitors; 900W. And, 3-4 minutes of run time in the midst of a frag fest isn't very much, so yes I think the UPS should be at least 900W, probably more like 1500W if you want reasonable run time.
 

danraies

Distinguished
Aug 5, 2011
940
0
19,160


Not to throw stones, but westom is just ranting about how much he hates UPSs and marketing strategies.

A UPS gives a voltamp rating and a wattage rating - the wattage rating is what you want to pay attention to. Westom is right that your computer often uses far less than the PSU rating, but if your PC is under load and the power goes out you're going to want a UPS that can support the draw. If you really want to be accurate, buy a wattage meter (http://www.killawattplus.com/), put your computer under heavy graphical load, and measure the draw. I would not advise a 500W UPS even though your computer usually draws less than 500W. You've got a pretty intense system and if the power goes out in the middle of a game you're going to want the UPS to keep up with it until you can shut down.

I don't have an oscilloscope, but that's my opinion.
 
What makes you think his system would only need 350W at peak? A GTX 580 is about 300W by itself, add in the CPU load and the rest of the system he will hit 500W under load with just one GTX 580 in it, when he adds the second one for SLI i would expect the DC load on the power supply to be around 600-700W.

If you honestly believe that a machine with 2 gaming video cards only needs about 250W then you need to catch up on tech.
 